Is it advisable to cast concrete column at half?

to the construction pros,

i work as a quantity surveyor . last week my site is having a concrete column casting. due to excess volume of concrete.. my site personnel so called "senior site supervisor" ordered the workers to pour it into another empty concrete column mould (which was not scheduled for concreting on that day)..

to my agony, he cast the column (size of 1.2m x 0.6 m x 2.7 m high) which support the loads of 20 storeys half way..and he insist to continue the other half on the following day..even my site resident structure engineer oppose such action.

casting half of the column and continue a day later..will result a cold joint in the middle of the column..and will greatly affect the strength of the load bearing column...

to your surprise, the senior site supervisor shouted at us and said " i have been supervising concrete casting for 30 years, i say can means can!"...

so in your opinion, since we can cast the whole column to full height why not? is it advisable to do so?
jonsoon no está en línea   Reply With Quote

Sponsored Links
 
Old April 16th, 2006, 12:52 PM   #2
Kit
arkitect
 
Join Date: Nov 2003
Location: Singapore / Melbourne
Posts: 1,320
Likes (Received): 0

I don't quite understand what you meant ny casting half way but columns are usually cast in sections. In fact, you don't usually structural members cast in full height at once.

Besides technical issues, there's the good o' "who's going to be responsible?" thingy to consider. If the structural engineer oppose to such a move, he/she has the authority to stop all works there and then. You site supervisor can have 2000 years of experience for all I care but is he going to put his name down on the paper?
Kit no está en línea   Reply With Quote
Old April 16th, 2006, 04:48 PM   #3
bustero
Registered User
 
bustero's Avatar
 
Join Date: Dec 2004
Posts: 5,561
Likes (Received): 2

I think you refer to the cast not being monolithic. In this case Kit is correct in that in a tall building you can't really cast the whole thing at once, assuming the correct ironworks are there, should be ok but of course this must be qualified depending on your situation.
__________________
towards a livable city...
bustero no está en línea   Reply With Quote
Old April 16th, 2006, 05:29 PM   #4
ch1le
always on
 
ch1le's Avatar
 
Join Date: Jun 2004
Location: tallinn/Tartu
Posts: 4,574
Likes (Received): 74

i think you both have misunderstood...

I think he is referring to casting moulds, where lets say some moulds were to be filled with conrete one day and the others a day later. Since they got leftover concrete, they poured half a mould full, so, the next day they would fill it fully, and the concrete would than set very unevenly...

Im no structural engineer, but its sounds fishy to me!
__________________
looking for a modern prefabricated home by top estonian and international architects (like MVRDV and NL architects!) - http://katus.eu/en

Also, we are awesome architects - www.sportsport.ee
ch1le no está en línea   Reply With Quote
Old April 16th, 2006, 05:33 PM   #5
D'Transporter
A Carolinian
 
D'Transporter's Avatar
 
Join Date: Dec 2005
Location: Heart of Cebu
Posts: 90
Likes (Received): 0

You're right Jonsoon, if possible to achieve maximum strength for the structure the base of the column should be poured monolithically with the beams, girders and floor slabs that it support but I have seen some contractors traditionally pour the column up to the base of the girder and beams as first stage and beams, girders and floor slabs as second stage.

Last edited by D'Transporter; April 16th, 2006 at 08:39 PM.
D'Transporter no está en línea   Reply With Quote
Old April 17th, 2006, 12:56 PM   #6
jonsoon
Registered User
 
Join Date: Apr 2006
Posts: 2
Likes (Received): 0

ch1le is right, exactly wat i am trying to said..the engineer advise us to cast it as a monolithic structure. usually we cast it this way, for example, the floor height is 3.2m and the beam size is 600mm..we usually cast it to the soffit of the beam (3.2m - 0.6m = 2.6m)..by the way, anyone have any technical informations regarding this issue? i wish to present it to my superior..
jonsoon no está en línea   Reply With Quote
Old April 17th, 2006, 04:19 PM   #7
Rachmaninov
Registered User
 
Rachmaninov's Avatar
 
Join Date: Aug 2004
Location: Hong Kong Special Administrative Region
Posts: 3,209
Likes (Received): 17

It depends. Just make sure that you don't cast it such that the cold joint is anywhere near the maximum bending moment.
Rachmaninov no está en línea   Reply With Quote
Old April 19th, 2006, 02:07 AM   #8
vvill
Registered User
 
vvill's Avatar
 
Join Date: Sep 2002
Location: London
Posts: 677
Likes (Received): 2

Quote:
Originally Posted by Rachmaninov
It depends. Just make sure that you don't cast it such that the cold joint is anywhere near the maximum bending moment.
then pressumably, the middle of the column is where the maximum bending moment is gonna occur.. mmm... dangerous stuff!
vvill no está en línea   Reply With Quote
Old April 19th, 2006, 07:43 AM   #9
Rachmaninov
Registered User
 
Rachmaninov's Avatar
 
Join Date: Aug 2004
Location: Hong Kong Special Administrative Region
Posts: 3,209
Likes (Received): 17

When architects decided to have tilted and curved columns or twisted structures then it isn't necessariy so.
Rachmaninov no está en línea   Reply With Quote
Old April 20th, 2006, 04:57 AM   #10
oracle
Registered User
 
oracle's Avatar
 
Join Date: Oct 2002
Location: Geneva Switzerland
Posts: 49
Likes (Received): 0

Are there chemicals you can apply to the unfinished, open section of the column before casting the second load, in a way that would eliminate the 'cold joint' ?

Let's say your guy decided to pour concrete into the mold, and then he realized he doesn'have enough to fill it up. It's 60% full. Then, he would spray paint the open surface with that chemical, which would then seal it for 24 hours or so.
oracle no está en línea   Reply With Quote
Old April 26th, 2006, 05:48 PM   #11
Ted Ward
Registered User
 
Join Date: Apr 2005
Posts: 253
Likes (Received): 0

This site contains a little bit about 'end of day' joints. The bit on 'construction joints' down the bottom is relevant.

http://www.pavingexpert.com/concjnt1.htm

Doesnt really answer the first question though.
Ted Ward no está en línea   Reply With Quote
Old April 29th, 2006, 06:22 PM   #12
Q 1
BANNED
 
Join Date: Apr 2006
Posts: 8
Likes (Received): 0

No problem i work with reinforced concrete. Just scabble the the top of previous pour before the next. Problems only occur when a fair face finish on the concrete is required.
Q 1 no está en línea   Reply With Quote
Old August 31st, 2007, 09:19 PM   #13
Lagoon
Registered User
 
Join Date: Aug 2007
Posts: 1
Likes (Received): 0

no problem

you can stop your concrete anywhere only you need to make rough surface and wet the surface before adding next day concrete
also make sure you have a clean surface no loose materials
Lagoon no está en línea   Reply With Quote
Old September 6th, 2007, 03:38 PM   #14
n4m3l355
Registered User
 
Join Date: Jan 2007
Posts: 201
Likes (Received): 0

If the column only gets pressure on it is not a problem, but if a momentum appears in the column you are in big problem nothing could solve this problem except from taking it down and redoing it. Since by a momentum it wants to twist at the weakest point since it will shift to there, and this will be at where the joint is, since concrete is reinforced to control that it will breakup there for sure (if the force is big enough).
Now another problem that might appear is the looks, if its a bare column in sight this will not look so pretty which might be a problem to the architect.
__________________
We only want you when you're seventeen
When you're twenty-one
You're no fun
n4m3l355 no está en línea   Reply With Quote
Old September 7th, 2007, 11:11 PM   #15
Gordon Freeman
Registered Winner!
 
Gordon Freeman's Avatar
 
Join Date: Jan 2005
Location: Vancouver, British Columbia
Posts: 109
Likes (Received): 0

hey, im a concrete formworker in vancouver, i dont see there being a problem as long as the reinforcing steel is still protruding out of the half cast column to connect the next half of the pour, 2.7m is not very tall so casting that in half a pour is not usual, as long as there are dowels sticking out of the column, and perhaps spray a bonding agent on the surface of the concrete it should be ok, however i would consult the engineer of the project
Gordon Freeman no está en línea   Reply With Quote
Old September 8th, 2007, 05:31 PM   #16
glitz_boy
Registered User
 
Join Date: Feb 2006
Location: Singapore - Surabaya
Posts: 1,042
Likes (Received): 2

wow ... its wrong thing to do ...
glitz_boy no está en línea   Reply With Quote
Old September 15th, 2007, 11:27 PM   #17
Gary_A_Hill
Registered User
 
Join Date: Aug 2007
Location: Oakland
Posts: 90
Likes (Received): 0

Seismic Considerations

I doubt if this would be allowed in California, and it doesn't seem to make sense in any region with seismic activity, because the joint must resist shear.
What jurisdiction is this in?
Gary_A_Hill no está en línea   Reply With Quote
Old September 17th, 2007, 08:42 PM   #18
Ted Ward
Registered User
 
Join Date: Apr 2005
Posts: 253
Likes (Received): 0

What is the shear force in the middle of a column?

There are so many differing opinions on this thread, right now i tend to believe Gordon Freeman - he appears to be one of the more informed contributors to this thread.
Ted Ward no está en línea   Reply With Quote
Old September 18th, 2007, 06:09 PM   #19
glitz_boy
Registered User
 
Join Date: Feb 2006
Location: Singapore - Surabaya
Posts: 1,042
Likes (Received): 2

shear force is definitely not zero.

frankly speaking, it can be done, yes but would need to ensure the cold joints/construction joints which happens on the column to be similar to monolithically casted column.
glitz_boy no está en línea   Reply With Quote
Old September 19th, 2007, 02:43 PM   #20
n4m3l355
Registered User
 
Join Date: Jan 2007
Posts: 201
Likes (Received): 0

Quote:
Originally Posted by glitz_boy View Post
shear force is definitely not zero.

frankly speaking, it can be done, yes but would need to ensure the cold joints/construction joints which happens on the column to be similar to monolithically casted column.
If the shear force is not zero depending on how big it actually is. But non the less a columnīs shear strength depends on the reinforcements since concrete canīt handle it. But the concrete itself has as well a margin in it though not to big. But I seriously doubt such situation would be safe. You dont have ESA or something to calc it through to compare the situations?
__________________
We only want you when you're seventeen
When you're twenty-one
You're no fun
n4m3l355 no está en línea   Reply With Quote


Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off



All times are GMT +2. The time now is 05:00 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
Feedback Buttons provided by Advanced Post Thanks / Like v3.2.5 (Pro) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd.

vBulletin Optimisation provided by vB Optimise (Pro) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd.

SkyscraperCity ☆ In Urbanity We trust ☆ about us | privacy policy | DMCA policy

Hosted by Blacksun, dedicated to this site too!
Forum server management by DaiTengu